240v 30 Amp GFCI Solution

Posted: Sun Mar 19, 2017 8:23 pm
by Johnnywhiskey
What is the best solution (cost effective) to put a GFCI into a 4-wire system (hot-hot-neutral-ground)?

I'm working out the logistics to going electric with my boiler (and beer brewing setup also) and would like to make sure there is a GFCI somewhere in the system. I'll be using a 4-prong dryer outlet that I'm currently not using, but want to add GFCI protection. I cannot seem to find a cost effective solution short of having an electrician replace the breaker with a GFCI breaker. Are there any inexpensive inline 240v GFCI solutions? There are tons of 120v GFCI inline breakers, but it seems like nothing for 240v.

Absent a better solution, do I replace the panel breaker with a GFCI breaker, or maybe put a GFCI breaker in my controller box?

Best, JohnnyWhiskey

Re: 240v 30 Amp GFCI Solution

Posted: Sun Mar 19, 2017 8:59 pm
by ShineRunner
I use a spa panel that my buddy gave me when they cut up their hot tub.. Works great.

Re: 240v 30 Amp GFCI Solution

Posted: Sun Mar 19, 2017 9:17 pm
by joeymac
Just replace the breaker with a gfci breaker yourself. They literally pop in and out. Wait for a bright sunny day, kill the main supply breaker, and then remove the breaker panel bezel. Unscrew the conductors for your outlet, pop out the old breaker, and snap in the new. Then just go in reverse hooking stuff back up.

Running a still is 10 times more complicated than changing a breaker.

Heads up though, most gfci two pole breakers are $70-$120... I really should install one on mine.

Re: 240v 30 Amp GFCI Solution

Posted: Tue Mar 21, 2017 4:28 pm
by Johnnywhiskey
Thanks guys. You confirmed what I was thinking. The GFCI breakers aren't cheap, but I'll have one installed. Probably use a electrician I know that is pretty affordable. If I'm going to install a safety device, I might as well make sure it is done right. Although the process looks pretty simple.

I thought about the spa panel solution, but I didn't want an extra box to deal with. Did you install your equipment in the spa panel or separately?

Best, JW

Re: 240v 30 Amp GFCI Solution

Posted: Tue Mar 28, 2017 7:46 pm
by Oldvine Zin
You can buy a lot of grain for what it cost to have a sparky install that breaker. They just snap in and out as joey said. But if you are totally unsure of your electrical abilities be safe and hire a pro.

OVZ

Re: 240v 30 Amp GFCI Solution

Posted: Tue Mar 28, 2017 8:17 pm
by RedwoodHillBilly
Oldvine Zin wrote:You can buy a lot of grain for what it cost to have a sparky install that breaker. They just snap in and out as joey said. But if you are totally unsure of your electrical abilities be safe and hire a pro.

OVZ
Not difficult to put in a 240v split phase GFCI breaker. There will be a neutral wire from the breaker, don't tie it to the neutral in the panel, it should go only to the load.

Re: 240v 30 Amp GFCI Solution

Posted: Wed Mar 29, 2017 12:43 pm
by Klein
RedwoodHillBilly wrote:
Not difficult to put in a 240v split phase GFCI breaker. There will be a neutral wire from the breaker, don't tie it to the neutral in the panel, it should go only to the load.

120/240
The white wire (neutral) that is built on the breaker goes to the neutral bar and the neutral from the load goes onto the neutral terminal on the breaker

Re: 240v 30 Amp GFCI Solution

Posted: Wed Mar 29, 2017 6:23 pm
by RedwoodHillBilly
Klein wrote: 120/240
The white wire (neutral) that is built on the breaker goes to the neutral bar and the neutral from the load goes onto the neutral terminal on the breaker
Ooops, you're right. It's been a while.

Re: 240v 30 Amp GFCI Solution

Posted: Mon Apr 03, 2017 1:34 pm
by Johnnywhiskey
I ended up have an electrician do it for me. The breaker cost more than the labor to put it in, and I wanted to make sure it was done right with the right part. I've got a pretty good grasp of how to replace a breaker, so its not the "totally unsure" part that stopped me--it was the "I think I know how to do this" part, but it better be done right because my live (and possibly my family's lives) might depend on it. So I think it was money well spent.

Our electrician is a semi-retired Italian guy, and he asked me what I was going to do with the outlet. I told him I was building a brewing box--which is partially true. The electrician then told me he makes wine--and then got a little smile and said he makes grappa too. So we had a good discussion about distillation techniques.

Stay thirsty, JW

Re: 240v 30 Amp GFCI Solution

Posted: Sun Apr 09, 2017 11:23 am
by Oldvine Zin
Johnnywhiskey wrote:
Our electrician is a semi-retired Italian guy, and he asked me what I was going to do with the outlet. I told him I was building a brewing box--which is partially true. The electrician then told me he makes wine--and then got a little smile and said he makes grappa too. So we had a good discussion about distillation techniques.

Stay thirsty, JW
:thumbup: :thumbup: Sounds like you made a good choice!