Solved an annoying electrical issue today

Fittings, parrots, packing, tooling and so on.

Moderator: Site Moderator

Post Reply
User avatar
GreenEnvy22
Swill Maker
Posts: 239
Joined: Thu Nov 14, 2019 3:25 pm

Solved an annoying electrical issue today

Post by GreenEnvy22 »

My boiler has a 4500w element in it, but I only have 12 gauge wiring in the garage, so can only pull 20 amps. I have two of the round resettable fuses/breakers inside the garage disconnect, one on each leg. This then goes into a breaker panel with a 20amp GFCI breaker for the still.
Anyway, when brewing or distilling, I've been tripping one of the two breakers in the cutoff, at oddly low power, like 11-12 amps. I thought I had some phantom drain somewhere in the garage that was causing it.

Today i shut off all the other breakers in the garage, I ran an extension cord from the house to keep the fridges cold (one food, one beer taps).
So the only breaker turned on was the still.
After 10 minutes or so, again the same resettable fuse tripped. So I grabbed a spare from the house, swapped it out, and voila, now I can run 16amps consistently. Identical models, one must just be defective or worn out.
Happy to have figured this out. Now I'm content with the amount of power available. Heating up 9 gallons from 15C to first drips took less than an hour.


Also got to test how my 55 gallon water drum would do for cooling water. It handed a 9 gallon and then an 8 gallon run back to back, and water was still ok at the end. I wouldn't have wanted to try a third run same day, but at least in the winter, I can do plenty. I have it outside the garage, and punched some cooling lines through the garage wall so I can keep the garage closed while I'm using it.
---
I have a 50L pot still with dual Liebig condenser.
I typically make Whisky, grappa, and brandy.
User avatar
jward
Site Donor
Site Donor
Posts: 151
Joined: Mon Mar 30, 2020 2:06 pm

Re: Solved an annoying electrical issue today

Post by jward »

GreenEnvy22 wrote: Sun Jan 03, 2021 7:31 pm So I grabbed a spare from the house, swapped it out, and voila, now I can run 16amps consistently. Identical models, one must just be defective or worn out.
Good catch. The first time I had a bad breaker I opened and thoroughly checked every outlet for any signs of overheating or arcing with lots of head scratching when everything looked great. It's good to learn to not trust a breaker any more than any other component. I like to do a test of the GFCI before firing up the burners too.
Jstroke
Site Donor
Site Donor
Posts: 391
Joined: Thu Mar 26, 2020 10:51 am
Location: somewherenorthahere

Re: Solved an annoying electrical issue today

Post by Jstroke »

Having a WW shop, I can attest that breakers wear out. The more you trip them, it seems the less it takes to do so.

Good for you for going down the rabbit hole.
If in doubt leave it out.