Hi,

I'm looking into buying a distilling controller. I need something that provides 22KW of power (4x5500W elements).

I found this one, but it only has 1 SSR and only supports 7KW.

https://www.auberins.com/index.php?main ... cts_id=690" onclick="window.open(this.href);return false;" rel="nofollow

The DSPR400 supports up to 6 SSR in parallel, so I guess I can use this as a starting point. Any guidance will be appreciated.

Thanks,
StillerBoy
Master of Distillation
Posts: 3387
Joined: Thu Dec 01, 2016 6:27 pm
Location: Ontario

Re: 22KW control panel build

Post by StillerBoy »

What is your application for, as 22kw is more that a hobbyist requires, so many will not respond to your question.. and a PID controller is not the best for distillation..

Mars
" I know quite certainly that I myself have no special talent. Curiosity, Obsession and dogged endurance, combined with self-criticism, have brought me to my knowledge and understanding "

– Albert Einstein
Subsonic Instability
Novice
Posts: 8
Joined: Fri Apr 21, 2017 9:56 am

Re: 22KW control panel build

Post by Subsonic Instability »

Birzzz wrote:Hi,

I'm looking into buying a distilling controller. I need something that provides 22KW of power (4x5500W elements).

I found this one, but it only has 1 SSR and only supports 7KW.

https://www.auberins.com/index.php?main ... cts_id=690" onclick="window.open(this.href);return false;" rel="nofollow

The DSPR400 supports up to 6 SSR in parallel, so I guess I can use this as a starting point. Any guidance will be appreciated.

Thanks,
Unless you actually need to precisely control more than 5500 watts, I might just control one element with a controller and the others with on/off switches.
Of course this only works if 5500 watts is sufficient to operate your still after warm up.

Can you tell us more about your setup?

Man, if'n I heated my keg still with 22Kw...
B up to temp in less than 5 minutes...lmao...

Sent from my SM-G950U1 using Tapatalk
User avatar
fizzix
Site Donor
Site Donor
Posts: 3698
Joined: Tue Dec 05, 2017 4:08 pm

Re: 22KW control panel build

Post by fizzix »

Plus you want your 22kW to be 80% maximum of total power available, so you're looking at a 28kW controller MINIMUM.
Always over rate your controller --don't match it.
Pikey
Site Donor
Site Donor
Posts: 2444
Joined: Sun Oct 16, 2016 3:29 pm
Location: At the edge of the Wild Wood

Re: 22KW control panel build

Post by Pikey »

Plus of course 22 kw is nearly 100 Amps even at 240 volts ! Need a decent sized wire and plugs etc - :shock:
Birzzz
Novice
Posts: 27
Joined: Fri Jun 30, 2017 4:47 pm

Re: 22KW control panel build

Post by Birzzz »

Hi,

it is indeed not destined to be for home usage. I'm just testing the waters, it's for a future project. The unit would control a 100 gallon stripping bain-marie still. You said PID are not good for distillation, can you elaborate?

Thanks,
User avatar
fizzix
Site Donor
Site Donor
Posts: 3698
Joined: Tue Dec 05, 2017 4:08 pm

Re: 22KW control panel build

Post by fizzix »

Birzzz wrote:You said PID are not good for distillation, can you elaborate?
Distillations are controlled by power input which in turn controls product output. Running by temperature is a futile effort, and PIDs control temperature only.
There is no Magic Temperature as it's a moving target. It would be great if we could set our stills for X°, but we just can't and expect success.
As the mixture boils and thus the components change and vaporize, so does the combo boiling point.

So continue looking for a power controller.
User avatar
rubelstrudel
Rumrunner
Posts: 511
Joined: Mon Jan 29, 2018 3:48 am
Location: Vestfold

Re: 22KW control panel build

Post by rubelstrudel »

You really do not need one single power controller for all elements.
You get yourself 4x 6kVA voltage regulators, or power regulators.
Each regulator controlling 1 element would give better en finer control over the heating than a single controller.

Thats what you want. Control over the power input in your system. Not trying to have the system maintain a specific temperature.
The whole point of a fractioning column is to maintain that temperature for you using the power equilibrium between energy input and energy removal.
Using a PID controller for heating will only result in oscillations in temperature removing any hope of a clean distillate.

Assuming that you are using 230v/5.5kw elements- thats a whopping 25A/230V fuse for each of these heaters.
I wouldn't run this on anything less than a 3x 4mm2 copper cable. If you're talking 110V that goes up again.

But you're probably talking about 3x400V 3-phase power supply here? Right?
Easier to run 3 or 6 heaters then, to get an even load.
But now we're into heavy duty electrician territory.