GFCI protection for fused home
Moderator: Site Moderator
-
- Novice
- Posts: 32
- Joined: Sat May 21, 2016 7:42 am
- Location: Southern Indiana
GFCI protection for fused home
I am no electrician, but I do know that I want some protection in my still build. First, my build. 15 gal. keg with the Camco 5500W 220v element. My source for 220 is not on a breaker, but rather fused and I do not know the amps. I have to run a cord (8-3) outdoors to still. Does someone make in-line GFCI protection for my extension cord?
- Expat
- Distiller
- Posts: 2251
- Joined: Fri Feb 24, 2012 3:58 pm
Re: GFCI protection for fused home
Best option I can think of is to use a Spa GFCI. They're designed for outdoor use and usually manage up to 50amps.
Connect it in line with your outlet and this gives you a handy shut-off.
I would strongly suggest that you determine the amperage of the fuse before you do anything else. Make sure it doesn't exceed the rating of the wiring you have. 30a is sufficient for the element.
Edit: please remember I'm not an electrician, if you're uncomfortable with any aspect of the above, you should consult a licensed professional in your area.
Connect it in line with your outlet and this gives you a handy shut-off.
I would strongly suggest that you determine the amperage of the fuse before you do anything else. Make sure it doesn't exceed the rating of the wiring you have. 30a is sufficient for the element.
Edit: please remember I'm not an electrician, if you're uncomfortable with any aspect of the above, you should consult a licensed professional in your area.
_____________________
EXPAT
Current boiler and pot head
Cross flow condenser
Modular 3" Boka - pics tbd
___________________
EXPAT
Current boiler and pot head
Cross flow condenser
Modular 3" Boka - pics tbd
___________________
-
- Bootlegger
- Posts: 138
- Joined: Thu Mar 07, 2013 9:48 pm
Re: GFCI protection for fused home
You could get an in-line gfic like this. Unfortunately the 240v equipment is a lot more expensive than 120v.
http://r.ebay.com/AtLmUN
If you fuse is not rated to 30 amps, you run the risk of blowing it when you run the element. 5500w elements run about 21amps, plus you need a safety margin.
http://r.ebay.com/AtLmUN
If you fuse is not rated to 30 amps, you run the risk of blowing it when you run the element. 5500w elements run about 21amps, plus you need a safety margin.