Latching relay circuit to protect still

Post by Yummyrum »

Nothing new here but it was asked about in a recent topic so I thought I’d throw up some diagrams if others are interested .

The idea uses the simple latching circuit often seen where the big Red and green buttons are used to control a Contactor or heavy duty relay .
IMG_1438.jpeg
Although I’m using the Schnieder Contactor unit , a multipole relay can also be used if it has changeover contacts able to handle the element current .

A Contactor has sets of contacts that are moved when current flows in its Actuator coil . It is an easy way to switch 10s or 100s of Amps with just a small control current .

Many contactors also have a set of smaller Auxiliary contacts that are used for latching and control purposes .

You will see that the Contactor shown has three sets of 38 amp contacts ( the Six big arse screws on the base ) labeled L1 ,L2 , L3 then there are two Auxiliary contacts ( the smaller screws on the top left and middle ) . Finally , there is the Actuator coil connections on the right labeled A1, A2
IMG_1423.jpeg
The two Auxiliary contacts are different .One is normally Closed (NC) while the other in normally open (NO) .When the Actuator coil is energised , the contacts change.

Here is the basic latching relay circuit with a start /stop switch .
IMG_1428.jpeg
It is also worth pointing out that the big red switches are normally available with “Normally Closed “ contacts while the green ones have “Normally Open” contacts .

There is a good reason for this . :ewink:
IMG_1421.jpeg
IMG_1422.jpeg
So getting back to the Schematic .
When the green Start button is pressed , the circuit through the Actuator coil is complete and it “pulls in “ .

This is where the Auxiliary NO contact snaps closed . Now , if the Green button is released , the Auxiliary NO contact “holds” the relay ( Contactor) on . It is now latched on

It will stay latched on until the Red “Normally Closed” STOP switch is pressed . This resets the relay to it’s original state .

(If you click on the diagram , you will see a dotted line from the Actuator coil through all the contacts . This means that all contacts in that line will move accordingly)

This is where we can use the basic circuit and add extra “NC” circuits in series with the Red STOP switch to switch off the relay ( Contactor) if say , the coolant flow is too low …..or…. The temp at the too of the RC is too high ….. or…. the level in the boiler is too low ….etc .
IMG_1429.jpeg
It is also a quick check when you attempt to “fire up” the elements .
Unless all the safety checks are OK , the element won’t switch on .
IE , if the boiler isn’t full or the coolant flow isn’t sufficient .




OK , a bit more detail . The big red and green switches usually have a light in them as well . So when you hit the Green button , its light glows Green . When you hit the STOP button … or something triggers a shut off , the Red button glows .

These buttons have lamps built in and powered via seperate terminals . The Lamps can be of a variety of voltages , but 24 , 48, 120 and 240 are common .

The Contactor coils also come in a variety . Again , 24, 48, 120 and 240 are common .
Note that the Contactor coils are generally AC . This is very important . If you hook them up to DC , they will burn out in a matter of minates . ……Be warned …. :esurprised: ( Coils have inductance and that limits the current flow . If it says AC , it means AC).

Getting back to the lamps in the switches .

The Auxiliary contacts have been setup so that they can also switch the supply to the Lamps as well as providing the latching function .

All this could have been done at higher voltage . But if we are going to have cables running to flow sensors and Over temp sensors , having a nice low 24V AC is a great safe option . :thumbup:

I have bot shown connections to the Main contacts . It is intended that this unit goes before any controller or elements and the main contacts would feed such circuits .
User avatar
shadylane
Master of Distillation
Posts: 11266
Joined: Sat Oct 27, 2007 11:54 pm
Location: Hiding In the Boiler room of the Insane asylum

Re: Latching relay circuit to protect still

Post by shadylane »

I also use a latched relay for the power to the still.
There are two STC-1000 temp controllers with the contacts in series with the relay coil to shut off the power if the output end of the product condenser gets hot or the boiler exceeds 210'f
The reason I did it this way was to make the still as stupid proof as possible. I figure anything that limits drama is good. 120v is used for the control circuit, a 24v stepdown control transformer like your using would have been better. But my rig doesn't have any remote wiring like switches to worry about. There's power into and out of the box but the other wires are just coming from low voltage thermocouples.
I did it this way based on simplicity and safety.
User avatar
NZChris
Master of Distillation
Posts: 13738
Joined: Tue Apr 23, 2013 2:42 am
Location: New Zealand

Re: Latching relay circuit to protect still

Post by NZChris »

When doing multiple stripping runs, I record the wash temperature when I finish the first stripping run, then program the still to shut down at the same temperature for the subsequent stripping runs. The ABVs of the strips are very close to the ABV of first strip.

Overly warm product at the spout will also shut the still down.
User avatar
Yummyrum
Global moderator
Posts: 8632
Joined: Sat Jul 06, 2013 2:23 am
Location: Fraser Coast QLD Aussie

Re: Latching relay circuit to protect still

Post by Yummyrum »

shadylane wrote: Sat Dec 07, 2024 3:11 pm I also use a latched relay for the power to the still.
There are two STC-1000 temp controllers with the contacts in series with the relay coil to shut off the power if the output end of the product condenser gets hot or the boiler exceeds 210'f
The reason I did it this way was to make the still as stupid proof as possible
Thanks Shady , that is the sort of things that I was thinking about . STC1000 are a perfect fit . :thumbup:
NZChris wrote: Sat Dec 07, 2024 9:30 pm When doing multiple stripping runs, I record the wash temperature when I finish the first stripping run, then program the still to shut down at the same temperature for the subsequent stripping runs. The ABVs of the strips are very close to the ABV of first strip.

Overly warm product at the spout will also shut the still down.
Great idea Chris , it was you saying recently about it that started this . Thanks for the elaboration .

BTW , it’s going to become part of my new controller so looking for suggestions on what you all have done .
Millbo
Novice
Posts: 4
Joined: Mon Feb 05, 2024 5:29 am
Location: NC

Re: Latching relay circuit to protect still

Post by Millbo »

Nice!
In the motor control world we call that sort of setup a collapsing circuit.
Attachments
Typical collapsing circuit
Typical collapsing circuit
Beware of false knowledge; it is more dangerous than ignorance.
~George Bernard Shaw
User avatar
Black Bull
Novice
Posts: 87
Joined: Fri Aug 16, 2024 11:54 pm
Location: The Brew Room

Re: Latching relay circuit to protect still

Post by Black Bull »

This be ok Yummy ?
https://www.ebay.com.au/itm/22586581605 ... ZZPWHTB0VE
and the switches, latching or momentary ?
I'm not fat, I'm in shape....Round is a shape
Getting old has whiskers on it !
Tammuz
Bootlegger
Posts: 147
Joined: Sat Sep 21, 2024 11:59 am

Re: Latching relay circuit to protect still

Post by Tammuz »

Now that solid state relays have dropped in price would that be a better choice for your controller.
NormandieStill
Distiller
Posts: 2075
Joined: Wed Dec 30, 2020 10:17 pm
Location: Northwest France

Re: Latching relay circuit to protect still

Post by NormandieStill »

Tammuz wrote: Sat Jan 04, 2025 11:40 am Now that solid state relays have dropped in price would that be a better choice for your controller.
SSRs are a great solution for power control and switching applications but they do not create the air gap necessary to declare something as off. A contacter will completely cut the power while an SSR can / will leave a small current flowing.

When I get my dream controller built (Probably not before the summer) it will be based around YummyRum's burst fire controller and will incorporate the safety features from this thread.
"I have a potstill that smears like a fresh plowed coon on the highway" - Jimbo

A little spoon feeding *For New & Novice Distillers
amh71
Novice
Posts: 41
Joined: Sun Apr 03, 2016 6:49 am

Re: Latching relay circuit to protect still

Post by amh71 »

In my experience an SSR will always fail on, so you may not ever be aware that your safety device is broken.

They are great for doing the control switching but need to be backed up by a good old fashioned relay on their input power.
User avatar
Yummyrum
Global moderator
Posts: 8632
Joined: Sat Jul 06, 2013 2:23 am
Location: Fraser Coast QLD Aussie

Re: Latching relay circuit to protect still

Post by Yummyrum »

Black Bull wrote: Fri Jan 03, 2025 9:45 pm This be ok Yummy ?
https://www.ebay.com.au/itm/22586581605 ... ZZPWHTB0VE
and the switches, latching or momentary ?
Blackbull , that is just a standard 2pole contactor .
While it is suitable for switching the main power , it does not have the extra auxiliary contacts to do the latching circuit .

It could be used , but you would need to using a second relay wired as a latching relay to drive it’s actuator coil .
User avatar
Yummyrum
Global moderator
Posts: 8632
Joined: Sat Jul 06, 2013 2:23 am
Location: Fraser Coast QLD Aussie

Re: Latching relay circuit to protect still

Post by Yummyrum »

amh71 wrote: Sun Jan 05, 2025 6:16 am In my experience an SSR will always fail on, so you may not ever be aware that your safety device is broken.

They are great for doing the control switching but need to be backed up by a good old fashioned relay on their input power.
I agree with this .
Infact while using my SSR a couple of weeks ago it did a weird thing where I had been running it at 100% for several hours while doing a stripping run . When I went to switch off the power , I could still hear the boiler running . So the SSR had somehow kept running even though there was no drive to it . I had to switch it off at the wall to stop it . This happened twice . Once it had cooled down it works normally .

But main point is that if I had been relying on that device to kill power , it could have ended bad .
amh71
Novice
Posts: 41
Joined: Sun Apr 03, 2016 6:49 am

Re: Latching relay circuit to protect still

Post by amh71 »

Yummyrum wrote: Sun Jan 05, 2025 1:49 pm
amh71 wrote: Sun Jan 05, 2025 6:16 am In my experience an SSR will always fail on, so you may not ever be aware that your safety device is broken.

They are great for doing the control switching but need to be backed up by a good old fashioned relay on their input power.
I agree with this .
Infact while using my SSR a couple of weeks ago it did a weird thing where I had been running it at 100% for several hours while doing a stripping run . When I went to switch off the power , I could still hear the boiler running . So the SSR had somehow kept running even though there was no drive to it . I had to switch it off at the wall to stop it . This happened twice . Once it had cooled down it works normally .

But main point is that if I had been relying on that device to kill power , it could have ended bad .
Not sure i would trust that SSR again.

It's a lesson I learnt some years ago, I replaced a failed relay in a kiln controller with an ssr, no safety relay on the controller. Big mistake, ssr failed eventually and kiln continously heated, was over 1100C when I spotted it, cost me a fortune to replace the elements but could easily have gone on to cause a fire had i not been there.

Only use controllers with a safety output now and that always drives a contactor relay.

These are PID type temperature controllers rather than the power controllers we use here but the safety principles are no different.
Tammuz
Bootlegger
Posts: 147
Joined: Sat Sep 21, 2024 11:59 am

Re: Latching relay circuit to protect still

Post by Tammuz »

I've used contact relays when switching high power. I have had more than 1 weld the contacts so it was locked on. I would think that if ssr were such a problem companies that build controllers like Auber Instruments would avoid using ssr's in their controller.
amh71
Novice
Posts: 41
Joined: Sun Apr 03, 2016 6:49 am

Re: Latching relay circuit to protect still

Post by amh71 »

Tammuz wrote: Wed Jan 15, 2025 9:01 am I've used contact relays when switching high power. I have had more than 1 weld the contacts so it was locked on. I would think that if ssr were such a problem companies that build controllers like Auber Instruments would avoid using ssr's in their controller.
A mechanical relay as a safety only sees one activation per session, hundreds or thousands less per session than a control relay so has a very much longer life, when it does go it will fail either on or off, a SSR will always fail on, certainly in the case of the dozens I have used or made for others.

The point was, whatever you use, have a safety device, be that a relay or a big red switch but an SSR is unsuitable to be that device.
User avatar
shadylane
Master of Distillation
Posts: 11266
Joined: Sat Oct 27, 2007 11:54 pm
Location: Hiding In the Boiler room of the Insane asylum

Re: Latching relay circuit to protect still

Post by shadylane »

By default mechanical relays win the latching job because they can have an extra set of normally open contacts.
99.9% of solid state relays don't.

As to SSR's failure mode it can fail on or off or somewhere in between.
The majority of the time it will fail open.
Mechanical relays fail closed more often than SSR's due to broken springs or the contacts welding together.