220VAC from Dyer outlet? What power controller ?
Moderator: Site Moderator
220VAC from Dyer outlet? What power controller ?
I am doing research on how to use the 220VAC from the dyer outlet to drive a 10-15G boiler.
what power controller works with that source and voltage to control a electronic unit like a digi boiler.
I feel pretty safe around 110V, but not so much around 220V.
what power controller works with that source and voltage to control a electronic unit like a digi boiler.
I feel pretty safe around 110V, but not so much around 220V.
Re: 220VAC from Dyer outlet? What power controller ?
Three or four wire dryer plug?
Re: 220VAC from Dyer outlet? What power controller ?
it has 4 , the bottom in in a L shape
I bet is on : Nema 14-30P 30A 125V/250V AC Plug, 4-Prong Dryer 30Amp ( this is the plug that is used in that socket on the wall )
I bet is on : Nema 14-30P 30A 125V/250V AC Plug, 4-Prong Dryer 30Amp ( this is the plug that is used in that socket on the wall )
Re: 220VAC from Dyer outlet? What power controller ?
If you want to purchase a controller search for Auber or Blichmann Power Controller.
There are a number of build threads on this forum if you have the skills to build one.
There are a number of build threads on this forum if you have the skills to build one.
- Salt Must Flow
- Master of Distillation
- Posts: 2601
- Joined: Sat Jan 29, 2022 2:06 pm
- Location: Wuhan China (Novel Coronavirus Laboratory)
Re: 220VAC from Dyer outlet? What power controller ?
That plug can accommodate any controller because it has two 120V hot wires, a ground wire and a neutral wire. The most basic controllers only need two 120V hot wires and a ground.
Now the question comes, exactly what boiler to you intend to use? If it will be a 240V DigiBoil like you mentioned, well that boiler just needs plugged in if you intend to use its onboard controls. It's onboard controls offer 2000w, 1000w, and 500w at the flip of a switch on the unit itself assuming that it does not incorporate a thermostat to control temperature. The 240V DigiBoil only requires two hot wires and a ground. You can install a 4 wire plug on the end of the DigiBoil's power cord, but you only need to wire the two hots and a ground for it to work as intended. I imagine you could buy an adapter that adapts 3 wire to a 4 wire plug.
Some people open up similar boilers, bypass the control mechanisms and use a separate controller to have full control over the heating element. If you plan to do this, you can use the most basic controllers (2 hots and a ground) or any modern controller (2 hots, ground and neutral).
I know this all might sound confusing, but it's really very simple. The presence of a neutral wire is the main difference. The neutral wire is very handy because it allows people to incorporate convenient things like a 120V cooling fan, 120V LED indicator lights, 120V electric alarm buzzers, etc... A little 120V computer fan powered by a Wallwart within the controller's enclosure keeps a SSR (solid state relay) or a SSVR (solid state variable relay) and the heatsink cool as it operates. Very important in my opinion. To wire a Wallwart, you just tap into ONE of the hot wires and the neutral wire. Some people use a 240V computer fan so that they do not require using a Wallwart. Some people like to incorporate a 120V receptacle with a switch to operate a pump for instance. That would use ONE hot, a neutral and a ground.
Last edited by Salt Must Flow on Mon Jan 13, 2025 12:02 pm, edited 1 time in total.
Re: 220VAC from Dyer outlet? What power controller ?
That is a great power source for a small still. If you are talking about the digiboil kettles you might want to do some reading about them here before you buy- they are thermostatically controlled with a number of preset heating levels, this is not ideal for distilling. What you will want is to have power input control not temperature control. There are people who have modified the wiring of these units to allow an external power controller, so that is an option if you are committed to that boiler, but you may want to look at what other options are available before you spend your loot. Some of the milk jug and keg conversions are probably a better choice for a boiler. There are a few really great power controller builds on this site and lots of support if you want to tackle a build of your own. It might be a bit of work but it is also a great way to learn about your system and how everything works, as well as a chance to get a better understanding of that 240V power, how it works.
If you have 15 minutes I highly recommend watching the excellent video on YouTube by "engineering mindset" titled - sub panels explained- why are neutral and ground separated? This visually explains power and grounding in a really clear way.
You can think of your boiler as a sub panel load with the heating element(s) as the circuits, and the power controller as a dimmer switch regulating the flow of power on a lighting circuit. The digiboil would be more like an electric kettle fully on or fully off depending on a thermostat to control it at a single set temperature.
If you have 15 minutes I highly recommend watching the excellent video on YouTube by "engineering mindset" titled - sub panels explained- why are neutral and ground separated? This visually explains power and grounding in a really clear way.
You can think of your boiler as a sub panel load with the heating element(s) as the circuits, and the power controller as a dimmer switch regulating the flow of power on a lighting circuit. The digiboil would be more like an electric kettle fully on or fully off depending on a thermostat to control it at a single set temperature.
Re: 220VAC from Dyer outlet? What power controller ?
I have experience with a 35L 110V digiboil, nice unit, when it gets to temp it turns off the fire. Then on again and off again.
My unit, elcheepo amozon, AC 110V 230V 10000W Voltage Regulator, Electronic Thyristor Voltage Regulator, SCR Voltage Regulator Dimmer, Motor Speed Controller , works great, I have set marks so I can turn the dial and get what I need out of it. One day I might invest in a 220vac unit.
it will boil my water faster and I can add seafood faster The controller I have only has two inputs and two outputs, the ground I use is the chassis of the unit. I added that for my own good. I am not sure if that unit would also be good for 220V.
Thanks for all your reply. I think one day I might try DigiBoil - 65L/17.1G (220V)
My unit, elcheepo amozon, AC 110V 230V 10000W Voltage Regulator, Electronic Thyristor Voltage Regulator, SCR Voltage Regulator Dimmer, Motor Speed Controller , works great, I have set marks so I can turn the dial and get what I need out of it. One day I might invest in a 220vac unit.
it will boil my water faster and I can add seafood faster The controller I have only has two inputs and two outputs, the ground I use is the chassis of the unit. I added that for my own good. I am not sure if that unit would also be good for 220V.
Thanks for all your reply. I think one day I might try DigiBoil - 65L/17.1G (220V)
Re: 220VAC from Dyer outlet? What power controller ?
Wow.... I have never distilled seafood...sounds interesting
So if I am understanding this correctly you are asking about how to tap a NEMA15-30R outlet so that you can use the higher ampacity of the circuit to run a 120V digiboil you are controlling with an SCR?
Totally not recommended but easy to do! We can even show you how...
But..... if you do tap into 30A of 120V and run it through your SCR , what do you think the wiring and element in a 120V boiler designed for max 1800 Watts will do when it is feed up to 3600W ?
So if I am understanding this correctly you are asking about how to tap a NEMA15-30R outlet so that you can use the higher ampacity of the circuit to run a 120V digiboil you are controlling with an SCR?
Totally not recommended but easy to do! We can even show you how...
But..... if you do tap into 30A of 120V and run it through your SCR , what do you think the wiring and element in a 120V boiler designed for max 1800 Watts will do when it is feed up to 3600W ?
Re: 220VAC from Dyer outlet? What power controller ?
my appoligies for being unclear,
I want to use a 220V boiler and was wondering how I can use a power controller with it.
I want to use a 220V boiler and was wondering how I can use a power controller with it.
-
- Distiller
- Posts: 2075
- Joined: Wed Dec 30, 2020 10:17 pm
- Location: Northwest France
Re: 220VAC from Dyer outlet? What power controller ?
Unless he changes the element, nothing at all. If you connect a 1.8kW element to a 16A supply or a 32A supply it won't change what it pulls. You're not pushing more electrons through it, just making them available if requested!
"I have a potstill that smears like a fresh plowed coon on the highway" - Jimbo
A little spoon feeding *For New & Novice Distillers
A little spoon feeding *For New & Novice Distillers
Re: 220VAC from Dyer outlet? What power controller ?
that is exactlly right... but it sounds like Planohog has a 110V unit and one day may upgrade to a 220V unit, but that he is asking about running his SCR on 220V with his current ( 110v ) unit... ( if I am misunderstanding , my apologies.. )
Which leads to the next part, Plano if you try to run your dual rated ( 110v/220v ) SCR on 220v it will run fine... you will need to confirm what voltage that 10KW rating is at..
BUT if you connect that 220v power to your 110v boiler element it will try to run at 4 times its rated power ( around 7200W ) before it and/ or the thermostatic control very quickly fails... and even worse, if the wiring is not correct ( ie: 220v to ground instead of neutral ) your boiler and anything else in the house attatched to ground like water taps, furnace, appliances etc. Potentially could be energized without the breaker tripping!
If what you were asking was can you run a 220v digiboiler and 220v SCR controller from that NEMA 15-30R 220v dryer receptacle..yes it will work fine.
PS: if that is your dryer outlet I am going to assume you are in North America and residential power to our homes is 120/240V not 220V so it is best to buy components that are appropriate for your power supply.
Which leads to the next part, Plano if you try to run your dual rated ( 110v/220v ) SCR on 220v it will run fine... you will need to confirm what voltage that 10KW rating is at..
BUT if you connect that 220v power to your 110v boiler element it will try to run at 4 times its rated power ( around 7200W ) before it and/ or the thermostatic control very quickly fails... and even worse, if the wiring is not correct ( ie: 220v to ground instead of neutral ) your boiler and anything else in the house attatched to ground like water taps, furnace, appliances etc. Potentially could be energized without the breaker tripping!
If what you were asking was can you run a 220v digiboiler and 220v SCR controller from that NEMA 15-30R 220v dryer receptacle..yes it will work fine.
PS: if that is your dryer outlet I am going to assume you are in North America and residential power to our homes is 120/240V not 220V so it is best to buy components that are appropriate for your power supply.
Re: 220VAC from Dyer outlet? What power controller ?
copy on two legs of 120 out of phase.
Regards PH
Regards PH
- jonnys_spirit
- Master of Distillation
- Posts: 3916
- Joined: Wed Oct 21, 2015 7:58 am
- Location: The Milky Way
Re: 220VAC from Dyer outlet? What power controller ?
And neutral is the center tap "0V" from the transformer on the street - which should also be bonded to GND at service entrance. You can get two dedicated 120V 15A circuits from a 240V 30A dryer outlet if desired.
Cheers,
jonny
————
i prefer my mash shaken, not stirred
————
i prefer my mash shaken, not stirred
————
Re: 220VAC from Dyer outlet? What power controller ?
looks like a person would need this to use with the dryer outlet.
ONETAK NEMA 14-30P to 6-30R 240V 30 Amp 4 Prong Male Plug to 3 Prong Female Receptacle Generator Dryer Welder EV Charger Power Cord Adapter
- jonnys_spirit
- Master of Distillation
- Posts: 3916
- Joined: Wed Oct 21, 2015 7:58 am
- Location: The Milky Way
Re: 220VAC from Dyer outlet? What power controller ?
Or a standard cheap NEMA box with wirenuts inside. That's what I used and a dryer plug from home depot coming out one side with the wires to the power controller connected inside with the wirenuts. Dedicated dryer extension cable to the controller.planohog wrote: ↑Wed Jan 15, 2025 7:04 am 240VDB-65L-220_img5.jpg
This is what that boiler has, in the wiring diagrams seems to be 220-250 vac potential between the two lugs with one ground.
looks like a person would need this to use with the dryer outlet.
ONETAK NEMA 14-30P to 6-30R 240V 30 Amp 4 Prong Male Plug to 3 Prong Female Receptacle Generator Dryer Welder EV Charger Power Cord Adapter
Cheers,
j
————
i prefer my mash shaken, not stirred
————
i prefer my mash shaken, not stirred
————
Re: 220VAC from Dyer outlet? What power controller ?
Then somewhere between the wall and the boiler will be a power control to tune the temp you need without losing the heat source.
- shadylane
- Master of Distillation
- Posts: 11266
- Joined: Sat Oct 27, 2007 11:54 pm
- Location: Hiding In the Boiler room of the Insane asylum
Re: 220VAC from Dyer outlet? What power controller ?
The plug is 240v but what about the heating element?
I'd recommend using a ohm meter just to make sure.
Measure between the straight blades on the plug to see what the resistance is.
Once we are sure the heater matches the voltage, I'll draw a diagram on how to wire it to the dryer outlet.
Re: 220VAC from Dyer outlet? What power controller ?
Wait a minute... you said you had a 35L 110v digiboil..? This picture is not the plug that is on that unit is it...?