The idea uses the simple latching circuit often seen where the big Red and green buttons are used to control a Contactor or heavy duty relay .
Although I’m using the Schnieder Contactor unit , a multipole relay can also be used if it has changeover contacts able to handle the element current .
A Contactor has sets of contacts that are moved when current flows in its Actuator coil . It is an easy way to switch 10s or 100s of Amps with just a small control current .
Many contactors also have a set of smaller Auxiliary contacts that are used for latching and control purposes .
You will see that the Contactor shown has three sets of 38 amp contacts ( the Six big arse screws on the base ) labeled L1 ,L2 , L3 then there are two Auxiliary contacts ( the smaller screws on the top left and middle ) . Finally , there is the Actuator coil connections on the right labeled A1, A2
The two Auxiliary contacts are different .One is normally Closed (NC) while the other in normally open (NO) .When the Actuator coil is energised , the contacts change.
Here is the basic latching relay circuit with a start /stop switch .
It is also worth pointing out that the big red switches are normally available with “Normally Closed “ contacts while the green ones have “Normally Open” contacts .
There is a good reason for this .
So getting back to the Schematic .
When the green Start button is pressed , the circuit through the Actuator coil is complete and it “pulls in “ .
This is where the Auxiliary NO contact snaps closed . Now , if the Green button is released , the Auxiliary NO contact “holds” the relay ( Contactor) on . It is now latched on
It will stay latched on until the Red “Normally Closed” STOP switch is pressed . This resets the relay to it’s original state .
(If you click on the diagram , you will see a dotted line from the Actuator coil through all the contacts . This means that all contacts in that line will move accordingly)
This is where we can use the basic circuit and add extra “NC” circuits in series with the Red STOP switch to switch off the relay ( Contactor) if say , the coolant flow is too low …..or…. The temp at the too of the RC is too high ….. or…. the level in the boiler is too low ….etc .
It is also a quick check when you attempt to “fire up” the elements .
Unless all the safety checks are OK , the element won’t switch on .
IE , if the boiler isn’t full or the coolant flow isn’t sufficient .
OK , a bit more detail . The big red and green switches usually have a light in them as well . So when you hit the Green button , its light glows Green . When you hit the STOP button … or something triggers a shut off , the Red button glows .
These buttons have lamps built in and powered via seperate terminals . The Lamps can be of a variety of voltages , but 24 , 48, 120 and 240 are common .
The Contactor coils also come in a variety . Again , 24, 48, 120 and 240 are common .
Note that the Contactor coils are generally AC . This is very important . If you hook them up to DC , they will burn out in a matter of minates . ……Be warned ….
Getting back to the lamps in the switches .
The Auxiliary contacts have been setup so that they can also switch the supply to the Lamps as well as providing the latching function .
All this could have been done at higher voltage . But if we are going to have cables running to flow sensors and Over temp sensors , having a nice low 24V AC is a great safe option .
I have bot shown connections to the Main contacts . It is intended that this unit goes before any controller or elements and the main contacts would feed such circuits .