Hi,
Just purchased this drok led 4 in 1 multimeter, I am using it with Auber DSPR 1 Voltage Regulator, and quite happy with it, the only drawback is it shows the wrong Amp or Watt, the watt looks ok because this regulator is linear I tried it with a small kettle first to see in how many minutes it will boil the water for example it boiled 1 lt of water in 4 minutes at 100% power and when I did boil the same amount of 1 lt water at 50% it did it in 8 minutes so I can say that it is linear, and the watt is also cut by half but please look at the pic the amp is showing 5.08
Volt: 223.8
kW: 780
So Watt / Volt : Amp
780 / 223.80 = 3.48 amp but it displays 5.08 I do not know why it does that I use the DSPR 1 in burst firing mode anyone faced a similar problem ?
how can I correct it ?
My Multimeter reading wrong Amp
Moderator: Site Moderator
-
- Trainee
- Posts: 895
- Joined: Mon Mar 13, 2017 9:48 am
-
- Trainee
- Posts: 895
- Joined: Mon Mar 13, 2017 9:48 am
Re: My Multimeter reading wrong Amp
The error reading the power is because of burst firing mode. The meter has an averaging time that is less than the burst period. I'll bet if you watch the meter, you'll see the power output varying over time. Bottom line, don't worry about it. The power output would be correct of you were using a simple phase angle controller (think light dimmer). The burst mode is more efficient and will create less noise on the AC line, therefore it is a better control algorithm, but your meter isn't designed to read it correctly.
If it were me, I'd just remember where you set the controller for the product output that you want as an initial setting, and then adjust the power level of the still by look and feel.
If it were me, I'd just remember where you set the controller for the product output that you want as an initial setting, and then adjust the power level of the still by look and feel.
-
- Trainee
- Posts: 895
- Joined: Mon Mar 13, 2017 9:48 am
Re: My Multimeter reading wrong Amp
Thanks, I know where I set it last time dropped it to 16% and finished with 28% my element is 4500watt that part is ok but just wanted to see if I could do something about it there are true rms multimeters but I guess they would behave the same
Thanks Redwoodhillybilly
Thanks Redwoodhillybilly
Re: My Multimeter reading wrong Amp
Yup, a true rms meter would have the same problem.
You're welcome
You're welcome

- nuntius01
- Rumrunner
- Posts: 705
- Joined: Thu Jun 08, 2017 4:51 pm
- Location: upper midwest
Re: My Multimeter reading wrong Amp
and this is why we have this site. the amount of knowledge here really is top notch
I'm just the bank and the mule
post your still pics here
http://homedistiller.org/forum/viewtopi ... 16&t=66917
post your still pics here
http://homedistiller.org/forum/viewtopi ... 16&t=66917